We're straying a bit (a lot?) OT, but since it's safety related, hopefully
it will slide:
Dale wrote:
If your generator does not have 220V it would use a 3 prong.
The neutral on 120/240V generators are not at earth ground.
The fourth prong is earth ground on the gen frame.
It uses two seperate 120v circuits.
---
Depends on the generator. Some are isolated, some aren't, some have a
removable jumper inside, some have been modified one way or the other. Some
use a 3 prong non-grounding receptacle for 220V (Hot, Neutral, Hot).
There have been probably dozens of different receptacles used over the past
30 years for this kind of thing. There's at least 3 different series of
"twistlock" type connectors for instance, with half a dozen flavors within
a series for number of circuits, voltage and current ratings. When I worked
in the special effects business, we had bins full of a bewildering variety
of connectors with which we'd make up suicide cords and adapters. The
standard is that there is NO standard.
Particularly for generators that hams might come across from surplus or
used sources: If it's important, get an ohmmeter and check. Don't just
trust that the manufacturer did the "right thing", or that all the previous
users and owners did either. Do the subsequent users a favor, and label
the generator with what you find (along with the date!)
Jim, W6RMK