First off, I have been a broadcast engineer and consultant for about
forty years and a licensed commercial electrician for thirty years. I have
hardened many sites for lightning protection as part of the job.
Broadcasting facilities don't have the luxury of shutting down every time a
thunderstorm is forecast. We have to carry on.
A whole house surge protection will provide a degree of protection from
surges on the power lines, provided that it is installed properly according
to the instructions, normally attached directly to the entrance panel.
But it is only part of the protection plan. Don't bet the rent on it.
Protection at the equipment end is just as important. As hams we are
probably more exposed to damage from currents and voltages induced onto our
antenna structures by lightning than from those on the power lines. It's
along way from the back of the rig to the suppressor on the entrance panel
for a lightning induced current. The whole house surge suppressor will
probably do nothing for antenna system lightning charges.
(So, how do you know your protector is working if it fails open? If the
breaker tripped what does it mean? How do you test it? How many folks happen
to have a hi-pot tester laying around?)
As someone mentioned, lightning behaves much like RF. It has an RF
component broadly peaking from 100 KHz. to 500 KHz, but contains energy
literally from DC to light. RF hates ferrous materials and will usually take
a copper path if given a choice. I have solved several stations' lightning
problems simply by running all the feedlines and other cables to the tower
through four inch or so, EMT (electrical metallic tubing (steel)) used as a
choke. Of course these line are grounded at each end of the EMT. A little
series L, the conduit, makes the lightning seek an alternative path, the
ground rods at the base of the tower.
Probably as important as grounding is the concept of bonding everything
together so when one does get hit (not if) all the equipment rises and falls
at the same potential. I use copper straps from two to four inches wide for
my professional work. Then these straps all run to a common point ground.
Alternatively, one can use copper tubing if it is flattened at the end for
attachment purposes.
For a home station ideally all feedlines, including those for APRS, need
to come through a copper bulkhead that is properly bonded to the common
ground.
I do not normally use braided bonding cables, especially outside.
Exposed to the elements they oxidize in a few weeks or months and becomes
worthless for anything but DC current. (Well, the shields from real RG214
are probably OK for rig bonding as they're silver plated and used indoors.)
FWIW, the Polyphaser website has some very useful info about the
grounding picture and concepts.